Voltsafe aims to revolutionize shore power connectivity

Ben Stein

Ben Stein

Publisher of Panbo.com, passionate marine electronics enthusiast, 100-ton USCG master.

30 Responses

  1. Grant Jenkins says:

    Sounds promising Ben – heavily dependent on the monitoring technology, however….my first thought is what happens when the pedestal “detects” an anomaly, and shuts off the power to the boat – when nothing obvious is amiss. Will your average dock hand have the technical know-how to troubleshoot this?
    Also, I’m not clear on how you connect to it with a standard 30A cord – are they providing an adapter, or does it mean modifying your cord? And if the latter, how are you supposed to use your cord at traditional marinas?

    • Ben Stein Ben Stein says:

      Grant,

      You’re right that there is a possibility of false alarms, though at least you could be notified of the trip and deal with it before it results in dead batteries and spoiled food.

      There is a small puck that connects to the shore power end of a 30A cord. That puck then mates magnetically to the VoltSafe unit.

      -Ben S.

      • Grant Jenkins says:

        Thanks Ben, I see the puck in the pictures, wasn’t sure how it attached to the cord. So if the puck uses the standard twist-lock (kind of a misnomer, as it certainly doesn’t “lock”) of the original Hubbell design, then I’m not sure all that technology is going to help much. You still are dealing with the inherent physical deficiencies in the original connector, except now it’s between the male cord end and the female puck. Don’t mean to be a naysayer, and all the associated tech benefits are definitely cool – it just seems like the achilles heel of the physical connection still exists.

        • Ben Stein Ben Stein says:

          For now, there is still some of the achilles heel. But, bear in mind, the puck has a temperature sensor, so it will know if the connection gets hot. Hence, it will kill the power before a meltdown occurs. Otherwise, you’re right that for all the goodness the system could offer, VoltSafe needs to offer an end-to-end connection without any of the weak link connectors in place.

          Best,
          Ben

          • Trevor says:

            We also prefer to deliver the end to end solution (already designed). However, instead of forcing boat owners to spend more $ on yet another expensive electrical cord, we are first offering the inexpensive adapter to make use of their existing cord set. This is where the locking ring comes in handy on L5-30 corsets as we have a gasket that ensures significant water resistance between existing prongs when mated to our adapter (compresses gasket when screwing the locking ring tight).

    • VoltSafe provides adapters that locks (screw threads onto a boat owners existing L5-30 plug. VoltSafe tech does monitor over-voltage and over-current, but follows industry standards state by state when hard setting what our technology does in response. Grant, you are right to bring up concerns about nuisance tripping because that would defeat the benefits of the technology. The electrical fingerprint (adapter) must match within a preset tolerance of impedance and outside of this tolerance (a much higher resistance value would result in a potential meltdown. Instead your phone would instantly notify you to inspect and clean you contacts to resolve. One of the additional challenges we’ve continued to see play out in the marina ecosystem relates to better standards associated with reducing current leakage at marinas. Plenty of old boats and ones with poor upkeep that leak current into the surrounding water causing galvanic corrosion and ESD risk (especially in freshwater). VoltSafe tech shows real time current leakage from boats (through hot/neutral) and can also detect leakage from other sources (through ground) aka surrounding water. This allows us to create a leakage heatmap to assist marine electricians identify the source(s) of current leakage in their marina. Standards bodies have imposed adoption of ground fault circuit breaker.

      Trevor Burgess – VoltSafe CEO|Cofounder

      • Grant Jenkins says:

        Thanks Trevor – I didn’t realize the adapter thread-locks on to the existing L5-30 plug of the shorepower cord – that’s certainly an improvement. The rest of the technology sounds very promising. I share your concern about current leakage, and your system sounds a great way to track that down. Hopefully you can convince marinas to invest in the improved technology!

        • Trevor says:

          We (VoltSafe) are currently in Newport Oregon this week as part of the 50th annual Pacific Coast Congress of HarborMasters and Port Managers. We are actively pilot testing at many of these locations Port Authority locations. A big challenge they have relates to adopting the latest NEC 30mA ELCI (GFCI) requirements. Even if marinas are willing and able to absorb swapping $20 30a breakers with $250 ELCI 30a breakers, they still have the challenge of identifying the sources of current leakage and resolving. https://pccharbormasters.org/wp-content/uploads/2024/03/Newport-Draft-Agenda-V4.pdf

  2. Rich West says:

    It looks like I might not be the only one who’s backed out of the berth, forgetting to disconnect the power cord. I’m comforted!

  3. Bruce Pappas says:

    Until VoltSafe launches their boat-side solution, this product is highly dependent on marinas adopting this technology. So nothing for the average boater to look at yet.

    • Trevor says:

      Bruce, when we set out to deliver a shore power solution, we did so on the boat side first. In fact, the design is done and functional prototype tested (works really well). The product had L5-30 prongs that plug into normal pedestal and cord terminates with our native connector. Boat owners would need to retrofit their existing boat shore power inlet with an adapter (looks like a hockey puck) and voila! The product is already at the final stage of commercialization, but triggering this stage is the most expensive (>$1M in sunk costs) and as a startup company we needed to ensure we landed in the market correctly out of the gate. What we realized was that the marina operators needed the pedestal side solution even more than boaters.

  4. Dan Hendon Dan Hendon says:

    This sounds like great technology that won’t fly unless VoltSafe licenses the technology to other pedestal/cord manufacturers. Imagine all of us needing to carry the cord side of this device for the one marine we see with this tech or the one marina trying to manage their loaner devices for transients. Additionally, there are few marinas trying to upgrade their power distribution unless it is failing (as in on fire) or mandated. In Michigan, the state-run marinas are already changing to add the ELCI breakers, but since this is already being done VoltSafe is too late. Poor imagination on my part I’m sure but I don’t see how this gets rolled out. Maybe if all the manufacturers jump on . . .

    • Trevor says:

      Dan, I hear you and you absolutely bring up some great points. At https://www.voltsafemarine.com you will see the 3rd pic as you scroll down shows the simple adapter piece. It takes 10sec (5sec if your speedy) to lock it to a standard shore power cord and faster to remove. It also happens to be very inexpensive to replace. Marinas even use it for transients where the software does a CC pre-auth, just like a hotel does for a damage deposit in case they forgot to return. VoltSafe sits on the American Boating and Yachting Cousel and indeed more than 60% of marinas in North America have pedestals being >10years old. The new 2023 NEC mandate requiring marinas switch to using breakers (at the pedestal) that are (ELCIs) essentially Type B GFCIs that trip at 30ma in <100ms means every power outlet (30/50/100A) will need a matching ELCI breaker installed. So far only 4 out of 50 states have adopted this. Why? Because the damn ELCI breakers cost $250-$350/breaker (standard 30A breakers cost $20-30) which is ~$120k for a 400 slip marina just in breaker upgrades alone. Our units offer future proofing for when additional states continue to adopt the 2023 NEC code because the hardware inside our tech will serve as a 30A ELCI (but at no extra cost to customer).

  5. David Kerr says:

    VoltSafe may want to conform their pedestal to NFPA 70 National Electrrical Code which includes Article 555 Marinas, Boatyards, Floating Buildings, and Noncommercial Docking Facilities. It would be much better to adopt the current standard than to try to get it rewritten for their design. NFPA 555 is very specific and describes existing pedestal and receptacle designs in great detail. From the pictures, it seems VoltSafe didn’t address the electrical details and what NEC defines as a “Marine Power Outlet”.
    The technology looks great and it’s something that the big players like Eaton Marina Power should take notice of.

    • I would agree – I would think that NFPA compliance would rate MUCH higher with marinas (due to their insurance and state law requirements) than convenience of their customers. We are seeing the result of the NEC Art 555 30ma compliance in many newer marinas, and lots of boaters are unhappy about having to modify/repair their vessels to keep the ELCI breakers from popping – I’m not sure an additional layer of complexity wold be welcomed 🙂
      FWIW, its NFPA 303 that specifies the connectors, and since I can’t find an online copy (and I’m too cheep to spend serious money on one), I’ll leave that subject to others.

      Hartley

      • I went a bit further down this rabbit-hole.. I did find NFPA 303 online free (Thanks, NFPA!!) but they only include illustrations of pin & sleeve connections for 60 and 100 amp connections. For 30 & 50 amp connections, they refer to UL 231 and require UL listed components.
        UL 231 is not available online, so I couldn’t look any further (though they do refer to “locking” connectors).
        So it looks like if a marina wants to be NFPA (and , therefore NEC) compliant, they would need to utilize UL-listed connectors.

        Hartley

        • Ben Stein Ben Stein says:

          I think this is an interesting question and, at least in my opinion, a shame of a way for a potentially better connector to be stymied. I’ve reached out to Voltsafe to ask them about standard and code compliance. But, I’m also wondering about how something like SmartPlug would meet these same requirements.

          -Ben S.

          • Hi Ben! It looks to me like the NFPA and UL stuff applies ONLY to the shore side, while the much more voluntary ABYC standards apply to the boat side. This means that marinas are the tougher end of the equation – most will need to stay within their insurance requirements (which are likely to be tied to the NEC/NFPA standards).
            This may explain why SafePlug didn’t really go after the shore-end of the business – the regulatory hurdles may have been too tough/expensive to make it doable.
            I think it would be nice to have a safe “breakaway” shoreside connector – something less dramatic than destroying the connector or breaking the wires!

            Hartley

        • Trevor says:

          Indeed correct Hartley and there are nuances to these standards. All safety certified electrical products for sale in USA must conform to UL standards and in Canada CSA. which is different than actual safety certification testing to these relevant UL standards (which apply to the product in question). Testing can be done by any NRTL (Nationally Recognized Testing Laboratory) to UL standards. UL happens to also be an NRTL. https://www.osha.gov/nationally-recognized-testing-laboratory-program/current-list-of-nrtls

      • If i was a marina operator, I certainly would be frustrated with the added cost of ELCI breakers ($30 versus $300 for ELCI) AND the nuisance of trying to figure out the existing leakage sources from all the countless leaky boats in the marina. If a marine electrician just goes ahead and upgrades to ELCI breakers, likely the first thing will happen is that many branches of electricity will trigger the 30mA ELCI threshold immediately and he will then have to: 1) put the old breaker back in 2) test the water and boats slip by slip to pinpoint the source(s) of leakage 3) then figure out a remedy 4) once all fixed then re-replace the 30A breaker with the 30A ELCI breaker. So fun! VoltSafe Hardware and Software Solutions work together so that: marina operators can view the leakage at each slip in real time (due to the boat) AND leakage coming from other boats and/or sources (dock) into slip boat through earth. This real time data serves to create a marina leakage heat map that pinpoint the problems and is actionable for marina electricians at outset. We expect our hardware to also end up compliant as an 30A ELCI breaker also, meaning when you install a VoltSafe shore power unit you won’t need to also spend $300 on a 30A ELCI breaker. For states that currently haven’t adopted the 2023 NEC code, the VoltSafe ELCI breaker trip leakage is software tunable by the marina operator. For states that have already adopted the 2023 code, the trip leakage would be hard locked to match law at 30ma <100ms trip.

  6. David Kerr says:

    Voltsafe has great new technology for marina power management.
    Since any new commercial construction has to meet the State’s adopted NEC code version, Voltsafe might start by taking an already UL listed “marine power outlet” (pedestal) and adapting it for their improved connector and power monitoring. If it’s an enhancement to an already approved device, the Professional Engineer and the State Inspector would be more inclined to approve its use.

    • Trevor says:

      Agreed. Excuse the pun, but it’s shocking that only 4 of the 50 states have adopted the 2023 NEC code version, requiring marinas to use of Type B GFCI breakers (aka ELCI with 30ma trip in <100ms) at pedestals. The reality is that marinas in the other 46 states understandably don't want to replace $20 30A breaker with $250 ELCI 30A breakers, nor face the mess of current leaky boats. No doubt a huge PIA (pain in ass).

      Regarding safety certification to UL & CSA standards, VoltSafe does indeed have a path to (successful) certification.

  7. Grant Jenkins says:

    Good points all, but none of it eliminates the 1930’s Hubble twist-“lock” connector, which is the underlying weak point that makes everything else critical to preventing a disaster. As long as that’s part of the connection, we’re just treating the symptoms instead of the problem. I get that the industry and governments don’t want to legislate thousands of existing power cords unusable by mandating a long-overdue improved connector. But that’s ultimately what its going to take. Comparatively, many, many boat owners were forced to correct electrical issues on their boats to use newly-mandated ELCI-equipped marinas, and typically at much greater expense than a new shore-power cord….

  8. David, I doubt the pedestal is what needs to be listed, but rather the actual fixture (outlet itself) that has to be UL-listed. If the whole pedestal is listed, then none of the component parts can be changed without all-new testing.
    Grant, you’ve hit the nail on the head – we would ALL like to see something to replace the “twist-lock” connectors! But I suspect that they remain the only 30 – 50 amp connectors that meet the UL spec (I’d love to hear what that spec entails – especially the “locking” part!)
    In the mountaintop radio site biz, we used 15 and 20 amp “twist lock” fittings in some sites, mostly so we could mount the fixtures overhead, facing down. A normal 15 or 20amp fixture won’t reliably retain a plug like that unless you tie the cord up to the structure, but we had no issue with those sizes of “twist lock” actually locking. In my experience, the 30amp twist-locks don’t “lock” worth a hoot – I’m not sure if they just wear out, or if the design is deficient. 50amp fixtures are much better, probably due to the metal outer sheath, which is significantly stronger than the pins alone which the 30amp uses for support.
    We went to SafePlug for the boat end on our vessel, but the other end of the cord is still the olde 30a twist-lock stuff, and it is obvious that it is NOT an optimum solution, especially after a few years and lots of use.

    I’m thinking there is a lot of inertia involved here – the twist-lock fixtures are UL-listed, the design is no longer proprietary (so cheap to copy) and the marine market is not big enough to support the kind of investment needed to supplant the olde twist-lock standard.
    A potential manufacturer (like Voltsafe) has to be counting on being a sole-source provider for a long time in order to recoup the investment needed to get their stuff through the approval process – but us users would rather see something that is NOT “sole-source” to keep the costs down – a tough situation. One does wonder if the IEC series of connectors offers anything that would be approvable without the well-know issues of the twist-lock stuff?

    Hartley

    • Grant Jenkins says:

      Yes, a lot of inertia to be sure.
      You said you went to a “SafePlug” for your boat end – I’m guessing you meant “SmartPlug”? That’s what I did as well, at least one end is secure! My home marina pedestals have threaded fittings, so at least I can use the Marinco locking collars to secure that end – but many marinas don’t have that provision.
      I havent seen any IEC-style plugs that include a physical strain relief (like Smartplug), or even any kind of twist-lock retainer.
      If anyone knows the ins and outs of this, it’s probably SmartPlug – they’re the only ones that I know of who have developed a superior product. I just don’t think we’ll ever see it in widespread use among marinas unless it’s mandated by code.

      • Yes, I should have said “SmartPlug” 🙂

        The IEC connectors the Europeans are using (ex: https://www.eaton.com/content/dam/eaton/products/wiring-devices-and-connectivity/wiring-devices/pin-and-sleeves/16a-and-32a-iec-309-watertight-pin-and-sleeve-devices-spec-sheet.pdf ) are pin and sleeve – the same sort of design mandated for 60 and 100amp boat connections by the NFPA. They “lock” in with an external sleeve, similar to the screw-in collars in use on Marinco and others, but it appears to be a bayonet, not a screw thread (a good thing, I think!). Hard to say if they would meet UL 231 requirements.

        • Ben Stein Ben Stein says:

          I’ve reached out to and heard back from VoltSafe. They will hopefully be responding to this thread shortly. The response is likely a bit delayed due to their office being closed for the holidays.

          That said, I’m in total agreement with Grant and Hartley’s sentiments about the goodness of an improvement over the existing twistlock connectors in use in marine. I routinely explain to boaters that their melted shore power cord wasn’t the result of a short circuit or any other extraordinary event, rather just poor design and a little age. That explanation is usually met with either skepticism that I’m full of it or surprise that this is what we have to work with.

          I’m hopeful that something can be done to improve upon this and while it is indeed single source, I think what VoltSafe has designed improves upon the current circumstances in nearly every regard. Now we have to see if the approvals and code compliance can be sorted out.

          -Ben S.

          • David Kerr says:

            My experience with the Marinco and Hubbell shore power cords is that boat owners are prone to mis-using them. Often there is no strain relief at the pedestal and not enough slack between the dock and the boat creating undue stress on the connectors and eventually failure.
            My pre-departure checklist now includes turning off the circuit breaker in the pedestal before unplugging the cord at the boat.
            The more you learn about electric shock drowning (ESD) the more you find that it is preventable.